Trying to locate the orfice for the air conditioner has front and rear air need to change it built too much pressure on high pressure hose believe its plugged up and need to change also will I need to run somthing through the line to clean it out. You might ask how I know that it built up too much pressure on the high end well it blew up the high
pressue line.
mercury villager 2000 air conditioner
Re: mercury villager 2000 air conditioner
if your high side hose blew there are a couple of reasons that could happen. One is your high pressure got too high. That can happen it the system is overcharged, the orifice is plugged up, or the fan is not coming on...
another thing that can cause the high side hose to blow is if it was rubbing against something that caused a weak spot in the hose. That could cause it to blow without having excessive high pressure.
if you have front and rear air you should have two orifice tubes. the orifice tube should be between the condenser and evaporator. Look at the closest connection to the evaporator
another thing that can cause the high side hose to blow is if it was rubbing against something that caused a weak spot in the hose. That could cause it to blow without having excessive high pressure.
if you have front and rear air you should have two orifice tubes. the orifice tube should be between the condenser and evaporator. Look at the closest connection to the evaporator
Re: mercury villager 2000 air conditioner
Thanks I did find it and the orfice was plugged up only found one by the condensor put a new orfice on and it works great
Re: mercury villager 2000 air conditioner
what does it look like it was plugged up with?
Re: mercury villager 2000 air conditioner
It was black and some brown flakes of I don't know what.
Re: mercury villager 2000 air conditioner
that may be small pieces of the compressor sealing components being pushed through the system. there isn't anything you can do about it but just be aware that your compressor is getting worn.